Thread: IBC help

  1. #1

  2. Guest
    All the answers to your questions are in the instruction book, which should have been provided with the IBC. If you havent got one, it is available on the manufacturers here - http://www.robowars.org/docs/ibc-docs-v0.1.pdfhttp://www.robowars.org/docs/ibc-docs-v0.1.pdf

    From the manual:
    quote:

    #1 = +12v - This pin will provide a stable 12v output from the switch-mode regulator, regardless of
    the battery input voltage. Do not attach devices that use more than 300ma. Small relays and
    remote-power LED€™s (with a suitable resistor) can be powered from here.
    #2 = AUX High - An €œOpen Collector to Ground€ output that will activate [internally connect to
    ground (-)] when the €œAUX1€ Servo input Joystick is more than 30% €œForward€. This output can be
    used to ground one side of a relay-coil to trigger weapons. The maximum current is 300ma. Use an
    intermediate relay if you require more current than this.
    #3 = AUX Low - The same as AUX High, but activates when the AUX1 input is more than 30%
    €œbackwards€
    #4 = +5v - This pin provides a regulated 5v output from the onboard 5v regulator, regardless of
    battery voltage. Do not attach hi-current devices to this pin. Suitable for small relays or LED€™s (with a
    suitable resistor) only.
    #5 = FLIP Input - an input that tells the controller to reverse its direction and steering controls if
    the robot is turned upside down. This can either be connected to a tilt-switch that grounds the input
    when the bot is inverted, or to either of the AUX High or Aux Low outputs for remote control of the flip
    function from the radio transmitter (if the 3 rd channel is not required for weapons). Do not exceed 5v
    on this input. FLIP is active when grounded (0v).
    #6 = Ground (Gnd) - Earth return point and ground reference for the Aux and FLIP inputs and
    Outputs. This should be used for any auxiliary connections rather than relying on the main power
    earth, since heavy current surges through the main cables can cause voltage fluctuations on the
    main earth point.

    A 60A fuse is a fair precaution, though a smaller one may be an option, depending on what youre running off it.